Deploy Site with GCP Console ClickOps
On This Page:
- Objective
- Site Types and Scenarios
- Considerations for Sites Behind NAT Gateway
- Prerequisites
- Procedure
- Create GCP VPC Networks
- Create Firewall Rules
- Import and Configure F5 CE Image
- Create Site Token
- Configure User Data for Virtual Machine
- Deploy Multi-Node Site
- Reserve External IP Addresses
- Create the F5 Customer Edge Node Instances
- Deploy Single-Node Site
- Create and Register Site
- Troubleshooting
- Concepts
- References
Objective
This guide provides instructions on how to create a customer edge (CE) site using the Google Cloud Provider (GCP) Console and deploy to a GCP VPC. For more information on sites, see F5® Distributed Cloud Site.
The scenarios below in the table have been tested successfully. The Network Address Translation Gateway (NAT GW) device in Table 1 references the GCP NAT Gateway. However, technically this should also work with third-party firewalls.
Note: In the
Number of Nodes
column,1/3
indicates 1 or 3 nodes. An App Stack site can be configured with up to 128 worker nodes total.
Provider | Site Type | Number of Master Nodes | Gateway Type | Interfaces | Scenario |
GCP | Mesh | 1/3 | Ingress | 1 | Mesh Single-NIC |
GCP | Mesh | 1/3 | Ingress/Egress | 2 | Mesh Multi-NIC |
GCP | App Stack | 1/3 | - | 1 | App Stack Combo |
In a regular deployment, each CE node has an External IP address associated with the Site Local Outside (SLO) interface, and the SLO route table routes the outgoing traffic via the Internet Gateway using the External IP address as the NAT IP address. But for scenarios where there is a requirement to have the CE site deployed without a public IP address, you can place the CE site behind a NAT Gateway. This can be the GCP Cloud NAT or any third-party instance, like a firewall used as a NAT gateway.
If you are deploying a site in this scenario, there are a few differences to note:
There is no public IP association with the CE(s).
You must ensure the CE can get to the Internet through its SLO interface.
From the GCP side, ensure that the routing table from the SLO subnet has a default route 0.0.0.0/0 that points to the NAT Gateway.
The NAT Gateway is a zonal object. In other words, it belongs to one availability zone. Therefore, in the case of a three-node CE cluster, you might want to deploy additional NAT Gateways for high availability.
Prerequisites
The following prerequisites apply:
A Distributed Cloud Services Account. If you do not have an account, see Create an Account.
An account with GCP. See Required Access Policies for permissions needed to deploy site. To create a cloud credentials object, see Cloud Credentials.
An official F5 Distributed Cloud Services GCP image.
Resources required per node: Minimum 4 vCPUs and 14 GB RAM.
F5 assumes that the resource group exists with a virtual network, including a minimum of two subnets: one for the Site Local Outside (SLO) and one for the Site Local Inside (SLI). The CE generally references the SLO interface as
eth0
and the SLI interface aseth1
For a single-NIC deployment (ingress gateway/Mesh or App Stack), only a single subnet (SLO) is required.
Internet Control Message Protocol (ICMP) needs to be opened between the CE nodes on the Site Local Outside (SLO) interfaces. This is needed to ensure intra-cluster communication checks.
Procedure
This procedure provides instructions for creating a Secure Mesh Site with two interfaces (ingress/egress) on a GCP VPC using GCP Console. Most of the objects and configurations are the same for single-node and multi-node sites.
Create two VPC networks to attach to the Site Local Outside (SLO) and Site Local Inside (SLI), respectively. Each of the VPC networks must have one subnet.
- In GCP Console, navigate to your VPC network.
![Figure Figure](/docs/static/a94cb09a1920e00556045a5c9d47a351/99e71/gcp-vpc-network.png)
- Click
CREATE VPC NETWORK
![Figure Figure](/docs/static/44f99fd42643848e640334375b15a719/99e71/create-vpc-network.png)
- In the
Name
field, enter a name for the outside network subnet, and then clickADD SUBNET
![Figure Figure](/docs/static/cf682d6a1621d3e20b5c752d644d8d6f/99e71/add-outside-vpc-subnet.png)
- Configure the outside subnet details, and then click
DONE
![Figure Figure](/docs/static/1b1308ee2e4be46e6540e871ca8021d3/99e71/config-outside-vpc-subnet.png)
- Keep other configuration parameters as default and click
CREATE
to finish.
![Figure Figure](/docs/static/e84ab406ae4ac9e009f856888a53c1c6/99e71/complete-outside-vpc-subnet.png)
- Perform the same procedure for the inside (SLI) network.
![Figure Figure](/docs/static/b48525393298852b75084a4b5e46ddfd/99e71/complete-sli-slo.png)
Create ingress and egress firewall rules for both inside and outside VPC networks (from the previous section).
Step 1: Configure ingress rules for SLI.
- For your VPC, locate and select the SLI network.
![Figure Figure](/docs/static/d8c2f5ba90ad795c0b55d6f23bf5fd53/99e71/locate-sli-subnet.png)
- Select the
FIREWALLS
tab, and then clickADD FIREWALL RULE
![Figure Figure](/docs/static/f05b5c3fe88bdb27f9d46cf8f4a93999/99e71/addrule-sli-subnet.png)
- Create
Ingress
rule for the inside network that allows traffic from the0.0.0.0/0
network to any target with tag:f5-ce
(create any tag name, as it will be used to identify the VM instance).
![Figure Figure](/docs/static/775cea56beab8b8c7ca1cb205a924955/99e71/ingress-rule-1.png)
- Under
Protocols and port
, selectAllow all
and clickCREATE
![Figure Figure](/docs/static/17a8122364e544c87756e615ac8ea172/99e71/ingress-rule-2.png)
Step 2: Configure egress rules for SLI.
Select the
FIREWALLS
Create
Egress
rule for the inside network that allows traffic to the0.0.0.0/0
network from target with tag:f5-ce
![Figure Figure](/docs/static/955ea4619de8dcd166004e5c4b68196a/99e71/sli-egress-rule-1.png)
- Under
Protocols and port
, selectAllow all
and clickCREATE
![Figure Figure](/docs/static/52bc323cb949bda9c9508de5f52baf95/99e71/sli-egress-rule-2.png)
- Verify the rules.
![Figure Figure](/docs/static/85205a9b3c8908a93d21dc62d1c71d93/99e71/sli-verify-rules.png)
Step 3: Configure ingress/egress rules for SLO.
Select the outside network and repeat steps 1 and 2 above to create the same ingress and egress rules for SLO.
Verify the rules.
![Figure Figure](/docs/static/2b9ff518d2602a8f4fded6c526fc0f25/99e71/slo-verify-rules.png)
Import the official F5 CE image file into GCP, and then configure its parameters.
Step 1: Download official image.
Image Type | Image | Cloud Storage File |
Mesh Single-NIC | rhel9-20240216075746-single-voltmesh | ves-images/rhel9-20240216075746-single-voltmesh.tar.gz |
Mesh Multi-NIC | rhel9-20240216075746-multi-voltmesh | ves-images/rhel9-20240216075746-multi-voltmesh.tar.gz |
App Stack Combo | rhel9-20240216075746-voltstack-combo | ves-images/rhel9-20240216075746-voltstack-combo.tar.gz |
- Navigate to F5 CE GCP Images and download the image file locally.
Step 2: Upload and configure image.
Images
underStorage
section inCompute Engine
![Figure Figure](/docs/static/1e4c5307dabfe64ed7172f48a52a605d/99e71/gcp-images.png)
- Click
CREATE IMAGE
![Figure Figure](/docs/static/86059d7590f4d257df6451c062bf8a55/99e71/create-gcp-image.png)
For the Mesh Multi-NIC image, use the following as an example:
Enter a
Name
. This example usesrhel9-20240216075746-multi-voltmesh-us-west2
For
Source
, selectCloud Storage file
Use the
Cloud Storage file
option to browse for and select the image file. This example usesves-images/rhel9-20240216075746-multi-voltmesh.tar.gz
For
Location
, select an option. This example usesRegional
For
Select location
, select your desired location. This example usesus-west2
For the
Encryption
option, selectGoogle-managed encryption key
Click
CREATE
![Figure Figure](/docs/static/813f395fe2640855cd8da72dcf9babef/99e71/create-gcp-image2.png)
Step 3: Verify image uploaded successfully.
Verify image uploaded and status is a green checkmark.
Create Site Token
Create a site token or use an existing token. If you are configuring a multi-node site, use the same token for all nodes. To create the token, see the Create Site Token guide.
Below is the cloud config user data example for the GCP VM instance that configures the VM.
#cloud-config
ssh_authorized_keys:
- "ssh-rsa XXXXXXXX mypublic-rsa"
write_files:
- path: /etc/hosts
content: |
# IPv4 and IPv6 localhost aliases
127.0.0.1 localhost
::1 localhost
127.0.1.1 vip
169.254.169.254 metadata.google.internal
permissions: 0644
owner: root
- path: /etc/vpm/config.yaml
owner: root
content: |
Vpm:
ClusterName: <site_name>
ClusterType: ce
Token: <site_token>
MauricePrivateEndpoint: https://register-tls.ves.volterra.io
MauriceEndpoint: https://register.ves.volterra.io
CertifiedHardwareEndpoint: https://vesio.blob.core.windows.net/releases/certified-hardware/gcp.yml
Kubernetes:
EtcdUseTLS: True
Server: vip
Change the following mandatory fields:
ssh_authorized_keys
: Enter your SSH public key. -
ClusterName
: Enter the site name for the site object created on F5 Distributed Cloud Console. This can be an App Stack Site or Secure Mesh Site. -
Token
: Enter the value for the site token created on F5 Distributed Cloud Console. This value is used to identify the tenant.
Follow these steps to create a multi-node Secure Mesh Site.
Create three external IP addresses and give each a name. These IP addresses are used later for the virtual machine instances.
- In
VPC network
, navigate toIP addresses
. Then clickRESERVE EXTERNAL STATIC IP ADDRESS
![Figure: Reserve External IP Address Figure](/docs/static/7776f6f1903e5eae76ba7058d33e07d3/99e71/config-rerv-ipaddr.png)
Enter a
Name
Under
Network Service Tier
, select an option. -
Confirm
Region
and other parameters are configured correctly.
![Figure: Reserve External IP Address Figure](/docs/static/b50ef57602469b130dc9f0c66555e6b8/14bc7/multi-site-reserve-ext-ipa.png)
- Repeat the above steps to create two more External Static IP addresses. For example, create
f5-ce-esip-02
andf5-ce-esip-03
for node two and node three of your site.
Create the F5 CE VM instances in GCP.
- In
Compute Engine
, underVirtual machines
, clickVM instances
![Figure Figure](/docs/static/99aa8af0e4419fe67e5b517da1bc31a7/99e71/gcp-vm-instances.png)
- Click
CREATE INSTANCE
![Figure Figure](/docs/static/07b55d6011b147bcc5794bdc2aad99f0/dcd69/gcp-create-vminstance.png)
- Use the following table help with the example parameters:
Parameter | Value | Notes |
Name | f5-ce-node-01 , f5-ce-node-02 , f5-ce-node-03 | Names of nodes for CE site. |
Region | us-west2 | Region from GCP. |
Zone | us-west2-a , us-west2-b , us-west2-c | Zones from GCP. |
Machine Configuration/Machine Type | n1-standard-4 | Recommended instance types are n1-standard-4 (4 vCPU, 15 GB RAM), n1-standard-8 (8 vCPU, 30 GB RAM), n1-standard-16 (16 vCPU, 60 GB RAM). |
VM Provisioning Model | Standard | Keep the default value. |
Confidential VM Service | Disabled | Keep the default value. |
Container | Disabled | Keep the default value. |
Boot Disk: Custom Images | rhel9-20240216075746-multi-voltmesh-us-west2 | Select CUSTOM IMAGES and use the image uploaded on the previous step. |
Boot Disk: Type | Standard persistent disk. | |
Boot Disk: Size | 80 GB | Minimum disk space required is 45 GiB for Mesh site and 100 GiB for App Stack Site. |
Identity and API access: Service Account | Compute Engine default service account. | Keep the default value. |
Identity and API access: Access Scopes | Allow default access. | |
Networking: Network Tags | f5-ce | Use the one created for the egress network firewall rule. |
Networking: IP Forwarding | Enable | |
SLO Network Interfaces: Network | f5-ce-outside-network | Outside network for eth0 . |
SLO Network Interfaces: Subnetwork | f5-ce-outside-subnet | Outside subnet created for outside network. |
SLO Network Interfaces: IP Stack Type | IPv4 | |
SLO Primary Internal IPv4 Address | Ephemeral (Automatic) | Use automatic IP addressing. |
SLO External IPv4 Addresses | f5-ce-esip-01 , f5-ce-esip-02 , f5-ce-esip-03 | Use the addresses created for the external IP address step. |
SLI Network Interfaces: Network | f5-ce-inside-network | Inside network for eth1 . |
SLI Network Interfaces: Subnetwork | f5-ce-inside-subnet | Inside subnet created for inside network. |
SLI Network Interfaces: IP Stack Type | IPv4 | |
SLI Primary Internal IPv4 Address | Ephemeral (Automatic) | Use automatic IP addressing. |
SLI External IPv4 Address | None | No external IP address for eth1 . |
Security: SSH key1 | <your_ssh_public_key> | Add your SSH public key to access the site admin CLI. |
Management: Metadata | Key 1: VmDnsSetting with Value 1: ZonePreferred | Zonal DNS mitigates the risk of cross-regional outages and improves the overall reliability of the VM. |
Management: Metadata | Key 2: user-data with Value 2: <cloud-config> | Use the cloud config user data created previously. |
- Enter VM name with desired region and zone. For machine configuration,
N1 series
is selected and the Machine Type isn1-standard-4
![Figure Figure](/docs/static/9b9ae2b1b40f7e03eb7d86a815abebb1/99e71/vm-name-config-1.png)
- Select default values for
Availability policies
,Confidential VM service
andContainer
![Figure Figure](/docs/static/79d9023cd0d45e9f05d8f5aac493a6bd/99e71/vm-name-config-2.png)
- Click
CHANGE
to configureBoot disk
. SelectCUSTOM IMAGES
tab and use the previously uploaded F5 CE image withBoot disk type
asStandard persistent disk
![Figure Figure](/docs/static/7ba3dd295e7ab218fe02ba4283634040/99e71/vm-boot-disk.png)
and empty firewall configuration.
![Figure Figure](/docs/static/02442a64ebb2c9e29de40f714b2b43ad/99e71/vm-identity-api.png)
- For
Network
tags, use the network tag created during the VPC network configuration. EnableIP forwarding
![Figure Figure](/docs/static/adaed68f62e2ca47520fb7db5a126027/2ec2a/vm-networking.png)
- In
Network interfaces
page, first configure the Site Local Outside network that has Internet connectivity. Use the previously configured external static IP addresses for this interface. This interface will be discovered aseth0
on the VM.
![Figure Figure](/docs/static/0c2d2c14735c0c1801f457073f6bf6e9/14bc7/multi-site-vm-slo.png)
- Add another network interface for Site Local Inside network. This interface will be discovered as
eth1
on the VM. The SLI network does not require Internet connectivity.
![Figure Figure](/docs/static/45c6e77a67f272dbc5ea658c16c634ab/5b9f9/vm-sli.png)
![Figure Figure](/docs/static/04acbe5cb76a69b9a0f38200cd55f588/14bc7/multisite-vm-sli-2.png)
- In
Security
, configure the SSH Key that was also used during user data configuration in a previous step.
![Figure Figure](/docs/static/700a5d83611fc84cedce2b73c4483cc4/99e71/vm-ssh-security.png)
- In
Management
, add the two key-value pairs per the table above.
![Figure Figure](/docs/static/9546aefc08fbc02582fa237f9bad8762/ff858/vm-mngt.png)
Click
CREATE
Repeat the above steps to create two more VM instances for node two and node three, respectively. Ensure that you are naming the instances (
f5-ce-node-2
andf5-ce-node-3
), their zones, and the external IP addresses correctly.
Follow these steps to create a single-node Secure Mesh Site.
Create an external IP address and give it a name. This IP address is used later for the virtual machine instance.
- In
VPC network
Enter a
Name
Under
Confirm
Region
![Figure: Reserve External IP Address Figure](/docs/static/37d7a2151f64a5ca5cb13877a0d551f2/14bc7/reserve-ext-ipa-region.png)
Create the F5 CE VM in GCP.
- In
Compute Engine
, clickVM instances
- Click
CREATE INSTANCE
Name | f5-ce | Name of site. |
Zone | us-west2-a | Zone from GCP. |
Identity and API access: Service account | Compute Engine default service account. | Keep the default value. |
Identity and API access: Access scopes | Allow default access. | |
Networking: Network tags | f5-ce | Use the one created for the egress network firewall rule. |
Networking: IP forwarding | Enable | |
SLO Network Interfaces: IP stack type | IPv4 | |
SLO Primary internal IPv4 address | Ephemeral (Automatic) | Use automatic IP addressing. |
SLO External IPv4 address | f5-ce | Use the address created for the external IP address step. |
SLI Network Interfaces: IP stack type | IPv4 | |
SLI Primary internal IPv4 address | Ephemeral (Automatic) | Use automatic IP addressing. |
SLI External IPv4 address | None | No external IP address for eth1 . |
N1 series
andContainer
- Click
CHANGE
- For
Network
- In
Network interfaces
page, first configure the Site Local Outside network that has Internet connectivity. Use the previously configured external static IP Address for this interface. This interface will be discovered aseth0
on the VM.
![Figure Figure](/docs/static/ba6a08340032dc4e52e80911a8715891/99e71/vm-slo.png)
eth1
![Figure Figure](/docs/static/51e34e36867b5d1dd57a8f1a27600881/99e71/vm-sli-2.png)
- In
Security
- In
Management
- Click
CREATE
Follow the Secure Mesh or App Stack site creation guides to create a site object on F5 Distributed Cloud Console.
Troubleshooting
For troubleshooting and opening a support case, see the Troubleshooting Manual Site Deployment Registration Issues guide. It provides step-by-step instructions to debug and resolve the issues that may arise due to Distributed Cloud published Terraform errors, networking and security misconfiguration, or CE internal process issues. The guide also provides instructions for contacting the F5 Distributed Cloud Support Team if you are unable to resolve the issue.